Quote:
Originally Posted by scrapart
House selling is getting expensive for us. Our relocation company ordered home Inspection for us and the Inspector asked to install AFCI Arc Fault Circuit Interrupter device and Fire rated door between garage and house. Our current door is metal not wood. Isn't that good enough ?
My house was built in 1999 and hence these were not the building code requirement. What should I do to avoide these expensive installations.
Our relocation company would not contribute to closing cost unless we meet this requirement. Has anyone went through this kind of situation ?
|
Hello Scrapart,
Arc Fault Circuit Interruptors (AFCI) were only required on 15 and 20 Amp bedroom branch circuits since 2005. In the 2008 National Electrical Code (NEC) they mandated them for all 15 and 20 Amp branch circuits in the home. However, your home was built in 1999 and predates these requirements. Unfortunately in the 2008 Rule Making Sessions/Law Changes the Texas Real Estate Commission (TREC) Inspector Advisory Committee (IAC) made a rule change requiring that all homes, regardless of their age, be compared to the 2008 NEC as far as AFCI's are concerned. Hence 99.9999999% of the homes in your area, 75019 Zip and Texas, are having their electrical systems marked as "Deficient" during a TREC controlled inspection. You can read the guidelines and rules for Inspectors here
TREC - Rules Governing Inspectors.
AFCI's are a safety item and would be "Nice" to have on all 15 and 20 Amp branch circuits. However, it was only required in 2008 NEC and unless the State mandates that all homes be updated then it really is not a fair item to mark on homes being inspected which pre-date these requirements.
I am not sure why your steel door is being written up as not fire rated. This is the actual building code reference for what the code requires on a garage door:
Quote:
R309.1 Opening protection. Openings from a private garage
directly into a room used for sleeping purposes shall not be permitted.
Other openings between the garage and residence shall
be equipped with solid wood doors not less than 1 3/8 inches (35
mm) in thickness, solid or honeycomb core steel doors not less
than 1 3/8 inches (35 mm) thick, or 20-minute fire-rated doors.
|
You would need to take a look at your door and see if it meets this requirement. The door itself can have no penetrations such as windows, animal access doors, etc. These are possible fire and smoke spread issue points.
If you have any other questions about your report please feel free to contact me. Good luck on selling the home and the move.